How many lug in the 400A trans-s cabinet?
I see there is note in 400A trans-s cabinet cutsheet. see picture.
I though it is one big lug up to 600MCM. or 2 small lug up to 250MCM. if it is correct.
Then I think I can have 1 set #1 and 1 set #10 to feed two equipment downstream.
Or I only able to feed one equipment downstream with max 2set 250mcm?
or 2 set for 2 equipment.

1740666873209.png
1740666886692.png
 
Some lugs (commonly on breakers) have an oval shaped opening and are rated for (2) small conductors or (1) large conductor, which is what the specs is addressing. Check with the ATS manufacturer.
 
How many lug in the 400A trans-s cabinet?
I see there is note in 400A trans-s cabinet cutsheet. see picture.
I though it is one big lug up to 600MCM. or 2 small lug up to 250MCM. if it is correct.
Then I think I can have 1 set #1 and 1 set #10 to feed two equipment downstream.
Or I only able to feed one equipment downstream with max 2set 250mcm?
or 2 set for 2 equipment.
The smallest conductor permitted on either of those lugs is 4 AWG.
 