I am installing a circuit for a new hot tub on an existing enclosed porch. There is a ceiling mounted light fixture above one side wall of the tub. The ceiling is 7' 10" above finished floor. The light fixture is being installed by others, but it will be not less than 7' 6" AFF.
So where is this 7' 6" height measured from? The water? The top edge of the tub? The floor?
In my case am I going to need to have them change the light fixture to meet (c) (2) below?
680.43 (B) (1)
(b) With GFCI. Where GFCI protection is provided, the
mounting height shall be permitted to be not less than 2.3 m
(7 ft 6 in.).
(c) Below 2.3 m (7 ft 6 in.). Luminaires meeting the
requirements of item (1) or (2) and protected by a groundfault
circuit interrupter shall be permitted to be installed less
than 2.3 m (7 ft 6 in.) over a spa or hot tub:
(1) Recessed luminaires with a glass or plastic lens, nonmetallic
or electrically isolated metal trim, and suitable for use
in damp locations
(2) Surface-mounted luminaires with a glass or plastic globe,
a nonmetallic body, or a metallic body isolated from
contact, and suitable for use in damp locations
So where is this 7' 6" height measured from? The water? The top edge of the tub? The floor?
In my case am I going to need to have them change the light fixture to meet (c) (2) below?
680.43 (B) (1)
(b) With GFCI. Where GFCI protection is provided, the
mounting height shall be permitted to be not less than 2.3 m
(7 ft 6 in.).
(c) Below 2.3 m (7 ft 6 in.). Luminaires meeting the
requirements of item (1) or (2) and protected by a groundfault
circuit interrupter shall be permitted to be installed less
than 2.3 m (7 ft 6 in.) over a spa or hot tub:
(1) Recessed luminaires with a glass or plastic lens, nonmetallic
or electrically isolated metal trim, and suitable for use
in damp locations
(2) Surface-mounted luminaires with a glass or plastic globe,
a nonmetallic body, or a metallic body isolated from
contact, and suitable for use in damp locations