Luminare T-code achieved with Zone protection installed in Division classified area

Status
Not open for further replies.

fun ee

Member
Location
Texas
A fixture is listed for both Class I, Division II and Zone 2. It can achieve a T3 rating using a Zone defined protection method "restricted Breathing". If this protection method is removed by the installer from the fixture it's T rating approaches T1. Here is the rationale for installing this fixture in Class I Division II area and taking credit for the zone defined protection method.

NEC 500.8 (A) Suitability
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Which of the Section 500.8(A) Subsections were you planning on using? Personally, I believe Section 501.5 would be a better application.
 