Lutron dimming ballast
chris kennedy
Miami Fla.
60 yr old tool twisting electrician
I'm looking for the spec sheet on a Lutron FDB-T432-120-2-5 dimming ballast. I don't see it on their site. I know it exists, I have 12 of them.
Thank you.
chris kennedy
Miami Fla.
You don't have that one.
You have a FDB-T432-120-2-S.
Click here.
Bottom of page 4.
So I should have been wearing my glasses.:roll:
Thanks Ken but the specs don't answer my question which is:
Can I hook up the black and orange leads up to undimmed 120V and get full intensity from the lamps?
480sparky
Iowegia
Picky, picky, picky! If I gave you a $100 bill, you'd complain it wasn't five 20s! :D:D
Ballast Test
DISCONNECT POWER by turning off the breaker. With the ballast properly wired to a fixture, connect the Dimmed Hot (orange) and input Hot (black) input to the Hot feed from the breaker. When power is re-applied, the lamps should go to full brightness. If the lamps do not come on at all, there may be a miswire condition on the lamp sockets or the ballast may be damaged or defective.
chris kennedy
Miami Fla.
You know how hard it is to break a $100 bill around here?
Ballast Test
Perfect, thank you sir.