Lutron
Lutron
We are both a home automation company, as well as an electrical contractor. We are very familiar with the Lutron system, and install these quite often in our area. The system is great, and is capable of doing an impressive array of things, but, like anything this complex, is worthy of doing your homework.
Keep in mind:
1. The lighting "loads" need to be carefully identified, isolated, and run as separate home runs all the way back to the panel. Instead of running switches, every light or group of lights becomes a load, and gets its own home run all the way back. Then, a low voltage- usually a Cat5e, is run from the same panel back to the switch location. Lots of extra wire, lots of extra labor.
2. Emergency stand-by generators tend to wreak havoc with the Lutron system. This is primarily because most standby units ave some Hertz variations, and the Lutron system requires a fairly stable 60Hz to maintain properly. Consider selling the customer on a back-up UPS for their components and system
3. Programming is computerized, and needs to be done by someone thoroughly trained in the software.
I'd be glad to answer any more questions, should they arise..