LV above Commercial Kitchen

Status
Not open for further replies.

DasMrDomo

Member
Location
FL
Occupation
M.E.P. Engineer
Hi all,

I ran into a bit of a gray area with low volt and kitchens, and would love some input on the matter.

We are converting portions of office space into a "kitchen", for that reason the space will need to be enclosed and fire rated to the decking. Unfortunately there is a substantial amount of networking and control LV above the ceiling tile for that area.

Am I correct assuming all that LV needs to be protected if it were to stay?
 
I assume this is a commercial job...Is that correct? Also is the ceiling a plenum? I assume nm cable like romex is not involved here.
 
I assume this is a commercial job...Is that correct? Also is the ceiling a plenum? I assume nm cable like romex is not involved here.
Commercial is correct, no Romex, all existing electrical is in MC conduit, but all LV is just sitting above ceiling tile. Ceiling cavity is not used as a plenum.
 
LV is fine except it may be required to be fastened. I have seen many jobs were the LV was just thrown up there and was lying on the grid. I believe you can just ty-wrap it to the ceiling wires. Some of the commercials guys should jump in here.
 