If the lv conductors are in the same conduit with the 120v conductors, they MUST have 120v insulation. 120v insulation does not exist. Standard power wiring has 600 volt insulation. So the monitoring/alarm wiring must also have 600v insulation.Originally posted by jlmiller:
Inside this one conduit is 3 runs of #12 thhn to tap off the 120vac feeding the strobe in order to power the monitor. Also inside this conduit are smaller conductors (cat 5, alarm wire, etc..using around 22-28awg) the pick up the form c relay contacts inside the strobe.
I'm sorry, but that is not completely correct. As Pierre pointed out in his post there are Chapter 7 or 8 rules that must be complied with.If the lv conductors are in the same conduit with the 120v conductors, they MUST have 120v insulation. 120v insulation does not exist. Standard power wiring has 600 volt insulation. So the monitoring/alarm wiring must also have 600v insulation.
and now, at the end of pg 1, I rest my case :roll:jb, I wish it were that simple, and if it is maybe someone here will teach me, but, i'm afraid you also must bring 725.25 and 725.55 into consideration. To be honest, I've struggle with Class I,II , II for years and still; don't think I have as full understanding.
Pierre,Originally posted by pierre:
My guess is the power is such, that the conductors off of the load side of the source will be required to be separated from the line voltage conductors.