LV Generator Grounding & Protection principles
sooria365
Hi All,
I am a new member to this forum. I would appreciate if any one can advise me on the following:
Application: 3 x captive generator (1680kVA each) with step-up transformer and connected to utility grid
1) What is the industrial norm for grounding an LV AC generator neutral? solid or isolated or through a resistance?
2) what is the recommended practice for protective relays in above cases?
3) There is a suggestion to go for device 59 (over voltage) relay fed from broken-delta on generator end and also for the HV side of transformer. Is it the correct practice?
Thanks in advance,
sooria -
You have definitely picked a non-trivial task. I suggest starting with IEEE 141 (red book), IEEE242 (buff book), and Blackburn, Protective relaying. This will get you a good start in understanding the physics.
I will attempt to answer your questions, but (mild disclaimer follows):
Without having the complete scope and specifics - I could be easily way off base. By choice, I'm not a designer. I'm a field dog. My work generally involves getting an installation, designed and build by others, to perform as needed by the customer.
sooria365 said:
1) What is the industrial norm for grounding an LV AC generator neutral? solid or isolated or through a resistance? ...
I tend to like impedance grounded. Boosts the reliability, cuts down on the damaging fault currents.
sooria365 said:
2) what is the recommended practice for protective relays in above cases? ...
There are a couple of common methods - The voltage levels and customer needs will dictate.
One can set up the relays to take a generator off-line if a GF shows up. If you are generating at 13.8kv then you want to get the gen off-line right away.
If you are generating at 480V and if continuity of power is required, then set the relays to annunciate only - and do an orderly shutdown on the gen. Then go look for the GF immediately.
sooria365 said:
3) There is a suggestion to go for device 59 (over voltage) relay fed from broken-delta on generator end and also for the HV side of transformer. Is it the correct practice? ...
Generating at 480V or 13.8kv? Utility is likely above 13.8kv - maybe 69kv or 138kv. I don't know where you are going to sync - Utility to xfm cb, gen cb?
There will be pts everywhere: Utility side of CB, transformer HV, transformer LV, gen. They are needed for the sync circuits and the protective relays.
Open-deltas for gen pts work fine and are fairly common (480V or 13.8kv). The HV (utility) pts will likely be wye connected and center-grounded. The gen open-delta pts will be corner grounded. Depending on where you are syncing there could well be phase shift issues to deal with.
There will be a dozen or so relays on the gen and the xfm. As for the specific question, you will want a 59 on the gen cb. You will also likely want a 59 on the utility cb.
Let us know how it turns out. It is an interesting project.
carl
Thanks very much Carl.
I will try to get hold of the reference books you have stated. As these generators are to be synchronised with Utility at 10kV, I am not sure what the utility requirements are with respect to protection, metering & control.
I shall keep you posted of the outcome (may not be soon due to lot of formalities with Client / Utility)
Cheers!
coulter said:
sooria -
carl
Hi Carl,
Thanks very much for your quick response. I will try to get hold of the books you have stated. The generators are rated 400V and being hooked up to 10kV utility lines through a YnY0 transformers. The utility requirements for paralleling these generators are still not clear. I will keep you updated.
Cheers!