In the '05 NEC, 411.4(B) says lighting systems operating at 30 volts or less are not permitted "Where installed within 10' of pools, spas, fountains, or similar locations unless permitted by Article 680".
Article 680.22(B)(4) says "Luminaires, lighting outlets, and ceiling suspended fans installed in the area extending between 5' and 10' horizontally from the inside walls of a pool shall be protected by a ground-fault circuit interrupter unless installed not less than 5' above maximum water level..."
Would you interpret this to allow LV fixtures between 5' and 10' from the inside of the pool below 5' as long as they were GFI protected?
Thanks
Article 680.22(B)(4) says "Luminaires, lighting outlets, and ceiling suspended fans installed in the area extending between 5' and 10' horizontally from the inside walls of a pool shall be protected by a ground-fault circuit interrupter unless installed not less than 5' above maximum water level..."
Would you interpret this to allow LV fixtures between 5' and 10' from the inside of the pool below 5' as long as they were GFI protected?