I've come across a strange installation where the client has run MV 4800V conductors through an existing 480V switchboard, and through the XFMR connected to the SWBD, to serve as the line side feed to an LIS that feeds the same SWBD and XFMR.
So two questions: 1) Can 4800V conductors pass through 480V SWBD and 4800V-480V XFMR? 2) If you open the LIS to de-energize the XFMR and SWBD, the 4800V conductors that pass through are still energized, is this allowed?