Disclaimer: Experience is Industrial only - mostly self generation
Always from the bottom up. The rest of this post is are just random thoughts - neither complete, nor rigorously true.
Coordination is defined as "daylight between the curves"
The MV feeder to the transformers has to be inside the transformer damage curve.
Sudden Over Pressure/Rapid Rise really aren't protecting the transformer. If these trip there is no transformer to protect, just a fire to put out.
All the main feeders - the trips have to be inside the cable damage curves
Ratios closer than 2:1 get hard to coordinate.
HRG gets rid of a lot of murderess, slow tripping, ground faults (480Y HRG)
Coordination down to the instantaneous range gets really difficult. If that is a must do, start looking at zones.
You can coordinate anything - it is just a matter of money.
Generators are difficult. The SCC is always low. HuH? why is that bad?
2MW, 480Y gen sub-transient reactance is ~ 20%. SCC is 12KA - not too bad
1MW, 480Y gen sub-transient reactance is ~ 20%. SCC is 6KA - This is getting in the range where the CBs may not trip quickly. Not bad, just have to pay attention.
Rest is not exactly part of the coordination:
Keep track of the Short Circuit Currents/Arc-fault. A 38 Cal/cm^2 fault while wearing a 40 cal/cm^2 suit, leaves the worker with survivable second degree burns. Maintenance switches to reduce arc flash are a good thing.
Low %IZ transformers SCC get insane really quick. For example:
1000 kva, 480Y, 5%IZ, SCC = 24kA, not bad
5MVA, 480Y, 7%IZ, SCC = 86kA, yuck
500kva, 208Y, 2%IZ. SCC = 69KA, yuck
Tell the designers to run the MV feeders out into the plant. Put smaller transformers out there - not one big one in the middle. When they tell you that is too expensive, tell them it is a $100M job, all you are asking for is $100.5M. And the life-cycle maintenance costs will more than pay off the small capital increase.