I've searched and searched and have not been able to get a satisfactory answer. For main lug only (MLO) panelboards/MCC, how high can I set the upstream feeder power circuit breaker for short-circuit protection? Let's say that the panelboard is stamped 65 kA (@ 3 cycles per UL). What is the highest instantaneous setting that can be applied to the upstream power circuit breaker? Furthermore, can I disable the instantaneous element all together and just use short time based on calculated I^2 x t?
It is interesting that panelboards/MCCs that are supplied with a main breaker, the instantaneous trip is set somewhere at 25% of kAIC rating. This is due to the limitations of molded case circuit breakers.
I've gone to the mfgrs, but all they will say is that the equipment is tested per UL.
Any suggestions and basis for these suggestions is greatly appreciated.