Apologize if this was covered before, searched and couldn't find the answer.
Trying to lay out circuits for 12v track lighting in a restaurant. For high voltage track, we have always allowed 75W per foot per 220.43. This lets you run 25' per 20A circuit.
For the 12v track; Considering that 300W is the largest circuit, using the same logic, we could only run 4' of track per transformer? 25' per circuit at 120v seems reasonable, 4' does not. :-?
I'm pretty certain that I'm mis-applying 220.43 here.
We have had inspectors verify on a number of installs that we have circuited 120V track for 75VA per foot, so if this is the wrong way to apply this article, the inspectors are doing it too.
Any thoughts?