I know where we stand on romex but can we bundle several ,lets say 20 runs of MC for 4 or 5 feet ?
Code referance if possible.
Code referance if possible.
I know I should know this, but where do we stand with romex on this subject?I know where we stand on romex
Kind of makes me glad I use MC much of the time.310.15(B)(2)(a)Exception No. 5: Adjustment factors shall not apply to Type AC cable or to Type MC cable without an overall outer jacket under the following conditions:
(a)Each cable has not more than three current-carrying conductors.
(b)The conductors are 12 AWG copper.
(c)Not more than 20 current-carrying conductors are bundled, stacked, or supported on ?bridle rings.?
A 60 percent adjustment factor shall be applied where the current-carrying conductors in these cables that are stacked or bundled longer than 600 mm (24 in.) without maintaining spacing exceeds 20.
please elaborate.Originally posted by jimwalker:
We are seeing very few jobs in emt anymore.Cost is far less but quality is suffering.Price seems to be only thing we care about anymore.
Whats wrong with Romex or some other premade cable? Its perfectly acceptable and well proven wiring method. Why spend more then you have to? I'd be willing to bet there are far fewer hiccups with the premade cabling systems then with EMT.Originally posted by jimwalker:
We are seeing very few jobs in emt anymore.Cost is far less but quality is suffering.Price seems to be only thing we care about anymore.
I don't see how this pertains to quality.Originally posted by jimwalker:
I am talking about looks as well as ease to add or change circuits
You would lose that bet I think.I have never had to tear a wall out to fix a piece of emt because of a sheet rock screw or nail.It is also a lot easier to replace a conductor in emt,which naturally goes to convenience and not quality.As far as quality goes,I suppose it doesn't matter which medium the conductor uses to get to where it's going,either one is going to be concealed in the wall.My opinion,MC is loved by Contractors because you can hire anyone to pull it,they have to know NOTHING about electrical work except how to strap it.That equals cheap labor,labor that I have to deal with,not the Contractor,the Engineer or the Inspectors.Journeyman/apprentice ratios are a thing of the past in many localities.Pride in your work is becoming a thing of the past with the new generation.I'm sure the 'old timers' said the same thing when I was starting the trade.I been here for 25 years watching it in the field,I feel I am very qualified to make these observations.MC is fine but the job that has to be installed in conduit,be it rigid or emt is better if nothing else because the guys who put it in more than likely knew how to do electrical work.Like I said in another post,I just had to fix several shorts on a job because of MC digging into the conductor,NEVER had to do that with EMT.I'd be willing to bet there are far fewer hiccups with the premade cabling systems then with EMT. [/QB]
I feel the same way. I'm only 25 but It's easy to tell when someone put pride into their work. And easier when they didn't. I make it a point on every job no matter how small. Bought the Jack Benfield guide on bending so when I have to work with emt or ridged it looks good and fits right. Personally I'd like seeing a good pipe job, just looks a hell of a lot more professional.Pride in your work is becoming a thing of the past with the new generation.
Well said,and I agree.Originally posted by pierre:
Fried
Every method has it's pros and cons, it all boils down to the installer. In the 30 years that I have in building construction, I have seen a trend, in general, of a lack in pride in what one does. Don't get me wrong, there are still some A-1 people in this industry, but there is a large influx of some who just don't give a 'hoot'.
I believe that the proper training in this industry is what is needed to help turn this trend around. Not just training in the electrical aspect, but training the men/women to understand what pride is. What the risks the employer takes everyday are. How his/her productivity can not only help the industry, but also increase their ability to earn more money.
I don't like the tone of that statement. I agree that it is important to take pride in your work; however, just because an MC or AC job doesn't look as pretty as and EMT or IMC job doesn't make it bad.I don't especially like it, but I'm beginning to come to grips with the idea that the bare minimum is what we are going to have to learn to deal with. As long as it is safe, and serviceable, I guess we have to accept it.