We are bidding an underground communications duct bank, the plans call for
(4) 3/4" inner ducts to be installed in a 4" pvc conduit. Question, What would the labor hours be for installation per 1000 feet?
 

360Youth

Senior Member
Location
Newport, NC
We are bidding an underground communications duct bank, the plans call for
(4) 3/4" inner ducts to be installed in a 4" pvc conduit. Question, What would the labor hours be for installation per 1000 feet?

I will be the first to tell you 2 things. 1) I have no idea. 2) The ones that do are going to want a whole lot more info than you have provided. :)
 

masterinbama

Senior Member
About the same as pulling 4- 4/0's in a 4". You also need to remember that innerduct will snag on anything. Use bell ends and lay your pipe in one direction, thinking ahead as to which way you are going to pull. Always pull towards the bell end of the pipe first, this will help eliminate snags.
 