I just got my Pv book in the mail. (xmas present to myself)
Flipping through it, I was reminded of a couple of code sections that I still struggle with.
First, I'm confused by the idea that somehow a supply side tap feeding an AC service disconnect doesn't
count towards the six throws of the hand. Utility power is brought to the line side of that disco, how are those conductors not SERVICE conductors? If you had 6 disconnects labelled Main Disconnect 1 of 6, 2 of 6, etc., seems like a bad idea to have a fifth disconnect supplying power to the building's wiring, even if that wiring is only connected to an inverter. This interpretation seems to defeat what I think to be the intent of the code, which the ability to kill ALL AC power to a buildings' wiring with six throws of the hand or less.
Second , and last for now, if a DC disconnect is required at a readily accessible location nearest the point of entry, then why the mention of wiring types to be used if a disconnect is not located nearest the point of entry?
I take this to mean 'A disconnect is required, but if you'd rather not install one, put the dc conductors in something metal.'
Thanks for your input.
Flipping through it, I was reminded of a couple of code sections that I still struggle with.
First, I'm confused by the idea that somehow a supply side tap feeding an AC service disconnect doesn't
count towards the six throws of the hand. Utility power is brought to the line side of that disco, how are those conductors not SERVICE conductors? If you had 6 disconnects labelled Main Disconnect 1 of 6, 2 of 6, etc., seems like a bad idea to have a fifth disconnect supplying power to the building's wiring, even if that wiring is only connected to an inverter. This interpretation seems to defeat what I think to be the intent of the code, which the ability to kill ALL AC power to a buildings' wiring with six throws of the hand or less.
Second , and last for now, if a DC disconnect is required at a readily accessible location nearest the point of entry, then why the mention of wiring types to be used if a disconnect is not located nearest the point of entry?
I take this to mean 'A disconnect is required, but if you'd rather not install one, put the dc conductors in something metal.'
Thanks for your input.