Ratings of ocpd's, bus, switchboard, and any other pertinent equipment not mentioned...???We have a M-T-M bus-way that ties two switchboards together in-case of loss of power feed to one the other picks it up. The A.H.J reviewer is arguing that the Tap rules 2008 N.E.C 240.21(B) apply and as such I should have an M-T-T-M arrangement. :huh: Do you agree?
Ratings of ocpd's, bus, switchboard, and any other pertinent equipment not mentioned...???
You can only have a tap situation if something is undersized for the ocpd supplying it.
GD covered the "physics".So if my tie OCPD matches the tie busway, then it is not a tap situation by definition? What section of the NEC made you come to this conclusion?