I've searched, but do not see the any results for the following topic:
Massachusetts amends the NEC (2017) to add a new section 210.25(B) to add a new section that reads:
"201.25(B)(5) Receptacles on Individual Branch Circuits. A receptacle outlet installed to comply with a requirement for an individual branch circuit shall contain a single receptacle, or a multiple receptacle if, and then only to the extent that, the supplied equipment inscudes multiple supply cord connections."
So my question to you all is, do you feel that applies to something like a refrigerator, a garbage disposal, a washing machine, etc? I don't believe that it does, as none of these circuits are required to to be on an individual branch circuit. For example the refrigerator. Providing that the load doesn't trigger an individual circuit, it could be on one of the 2 SABC's. If by design choice it is installed on an individual branch circuit, I don't see the above is applicable, so it can be on an duplex receptacle.
For another example, one of the newer style plug-in boilers used for heating equipment is required to have no other outlets, per 422.12, which reads
422.12 Central Heating Equipment. Central heating
equipment other than fixed electric space-heating equipment
shall be supplied by an individual branch circuit.
In this case, if the boiler is the only load, the receptacle must be a single receptacle.
Am I off base?
Any an all thoughts and opinions welcome.
TIA,
John422.12 Central Heating Equipment. Central heating
equipment other than fixed electric space-heating equipment
shall be supplied by an individual branch circuit.
Massachusetts amends the NEC (2017) to add a new section 210.25(B) to add a new section that reads:
"201.25(B)(5) Receptacles on Individual Branch Circuits. A receptacle outlet installed to comply with a requirement for an individual branch circuit shall contain a single receptacle, or a multiple receptacle if, and then only to the extent that, the supplied equipment inscudes multiple supply cord connections."
So my question to you all is, do you feel that applies to something like a refrigerator, a garbage disposal, a washing machine, etc? I don't believe that it does, as none of these circuits are required to to be on an individual branch circuit. For example the refrigerator. Providing that the load doesn't trigger an individual circuit, it could be on one of the 2 SABC's. If by design choice it is installed on an individual branch circuit, I don't see the above is applicable, so it can be on an duplex receptacle.
For another example, one of the newer style plug-in boilers used for heating equipment is required to have no other outlets, per 422.12, which reads
422.12 Central Heating Equipment. Central heating
equipment other than fixed electric space-heating equipment
shall be supplied by an individual branch circuit.
In this case, if the boiler is the only load, the receptacle must be a single receptacle.
Am I off base?
Any an all thoughts and opinions welcome.
TIA,
John422.12 Central Heating Equipment. Central heating
equipment other than fixed electric space-heating equipment
shall be supplied by an individual branch circuit.