MA Ammendment 406.9(C)

barkett519

Member
Location
MA
Occupation
Journeyman Electrician
Hello everyone just to clarify MA has ammended 406.9(C) making it code compliant to have a receptacle within 3 feet of a shower as long as it is not "within"? Can someone verify this inspector is telling me it cannot be within 3 feet and MA code guys out there. Thank you!
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Their amendments are online ... found this with a quick search:
406.9(C). Replace the entire content with the following sentence: "Receptacles shall not be installed within
or directly over a bathtub or shower stall."
 

Elect117

Senior Member
Location
California
Occupation
Engineer E.E. P.E.
lol

But in all seriousness, I thought that was the reason why. To limit the possibility of using plugged in items while in the bath / shower.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
lol

But in all seriousness, I thought that was the reason why. To limit the possibility of using plugged in items while in the bath / shower.
I think that is the intent but there has never been a limit of the distance that the receptacle has to be from the edge and even without the 3' rule is there any substantiation for the code change? Are there documented cases of injuries where the receptacle was say only 12" from the edge? The receptacle is already required to be GFCI protected.
 
Top