I got involved with a commercial job today where a 230V macerating pump is being installed for a sewer pit. The pump is cord and plug connected. The float switch needs to be hardwired.

Q: Can I hardwire the float to one side of the receptacle to control the pump? The float is single-pole. The plug will function as the disconnecting means.


Frank
 

kwired

Electron manager
Location
NE Nebraska
As long as the switch is rated for the motor, yes, otherwise you may need to use a relay/contactor to interface the two.
 