Machine disconnect behind guarding

Status
Not open for further replies.
Location
North Carolina
Occupation
Electrician
Good afternoon all. I’m working on a piece of OEM equipment that has their motor disconnect mounted behind a fixed guard. The guard has to be removed (it is bolted) to access the disconnect for the conveyor motor. I understand the definition readily accessible, but since this comes from the factory in this configuration, does this rule still apply?
Thanks
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Read carefully what 430.107 actually says.

It seems pointless to put a disconnecting means behind a guard, but I don't see that it is necessarily a code violation. I wonder if either the guard or the disconnect was added after the fact.
 
Location
North Carolina
Occupation
Electrician
Good point. I will check to see if the Motor controller disconnecting means is within sight of the equipment and can be locked in the off position. If so, I’m going to call it good.
 

BillyMac59

Senior Member
Location
Wasaga Beach, Ontario
Occupation
Industrial Electrician
The disconnect may be serving merely as an isolation switch for LOTO purposes. Is the guard merely a fence or does it have a safety interlocking switch to it. As stated in post #2, the guarding may have been added after the fact during a "risk assessment" review.
 

tthh

Senior Member
Location
Denver
Occupation
Retired Engineer
IMO, a conveyor disconnect should not be behind some guard that has to be unbolted. In my much younger days, I may or may not have seen someone on a conveyor trying to nonstick a jam up and the guy's foot got stuck between in the gap between two conveyors. Fortunately, I had work boots on and it didn't end badly.
 

retirede

Senior Member
Location
Illinois
IMO, a conveyor disconnect should not be behind some guard that has to be unbolted. In my much younger days, I may or may not have seen someone on a conveyor trying to nonstick a jam up and the guy's foot got stuck between in the gap between two conveyors. Fortunately, I had work boots on and it didn't end badly.

A properly installed conveyor system will have appropriately located E-stop buttons.

The purpose of a disconnect is not to to stop a machine in an urgent situation.
 

tthh

Senior Member
Location
Denver
Occupation
Retired Engineer
A properly installed conveyor system will have appropriately located E-stop buttons.

The purpose of a disconnect is not to to stop a machine in an urgent situation.
Ok, of course, makes perfect sense...I just went to my early life folly in my brain when I read this :)
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
A properly installed conveyor system will have appropriately located E-stop buttons.

The purpose of a disconnect is not to to stop a machine in an urgent situation.
I agree. Given the limited information we have been given to work with it is very hard to come up with a perfect answer.
 
Location
United kingdom
Occupation
Builder
Good afternoon all. I’m working on a piece of OEM equipment that has their motor disconnect mounted behind a fixed guard. The guard has to be removed (it is bolted) to access the disconnect for the conveyor motor. I understand the definition readily accessible, but since this comes from the factory in this configuration, does this rule still apply?
Thanks
I am also facing the same issue.
 

rambojoe

Senior Member
Location
phoenix az
Occupation
Wireman
I have seen some facility guys put discos in weird spots, just to shut down small parts of systems, which is why we say pics... Or it never happened. The kicker is, alot of places dont allow pics...
 