while i was in engineering today i learned that one line will have a 600 amp service and i am trying to figure out the system. any help would be greatly appreciated.
this system is a 480 volt 3 phase continuous operation powering (3)75 hp motors, (1)25 hp, (2)120 volt motors, and 2 transformers-(1)1.5kva and (1)3kva, and other small power components.
#1 if the system is rated at 214kw,244kva, and 310.5 full load amps, how do you get to 600 amps? 310.5 amps x 125% = 388.6 amps. so why can't we use a 400 amp busplug?
#2 if the system does require a 600 amp busplug, do i figure the service wire this way.
600 amp bus plug will require wire to the machine rated 125% above the 600 amps (600 x 1.25=750amps). if i run 2 sets of 500 mcm wire (3 1/2" rigid conduit per set),
430amps x .91 temp x .8 = 313 amps. 313 x 2 = 626 amps.
#3 how do you figure the service cable to the machine based upon bus plug rating?
thanks in advance