I am seeking some assistance in sizing wire sizes for a transformer that will supply power to a machine tool. I do not have a copy of the NEC code, so it's not that I am lazy and just won't look it up... The code book is on it's way, but I can't wait the week at this point, so I am hoping some nice folks here won't mind holding my had thru these calculations.
Project Scope:
I did the following:
With the help of this site http://www.mikeholt.com/mojonewsarchive/NEC-HTML/HTML/TransformerInstallation~20020516.htm I did the following calculations:
Primary Current: 54.1 amps
Secondary Current: 124.9 amps
Primary Current Protection: 54.1*1.25 = 67.7 -> Next size up is 70 amp (Class J fuse is required).
Primary Conductor Size (Table 310.16)(will be using THHN, 90?C, copper): 6awg
Primary Ground Size (Table 250.122): 8awg
**I have control of the wire type after the fusible disconnect, but before will be whatever the plant uses. Typically they use a cable, so in order to ensure adequate ampacities - should i spec the wire size and type taking into account the 80% correction factor (see below about wires in raceway/cable)?
Secondary Conductor Size(will be using THHN, 90?C, copper): ??awg
My next big area where I am confused is grounding/bonding.
Lastly, the machine tool came from the factory wired with 3awg (25mm?) wire from the MCCB to the first device (which is then daisy chained to other devices). I cannot see how this is ok as the ampacity of 3awg is 110amp at best (THHN @ 90?C). I would think I need to replace this with larger wires so that they are protected by the MCCB.
Sorry for the lengthy post. I just wanted to try and be as clear as possible and also show that I am trying to logically work thru this and not just get someone else to do all the work from me. Thanks for any and all help, I appreciate it!
Project Scope:
- We are outfitting a vertical machining center (standard machine tool) that runs on 208vac with a 480vac -> 208vac transformer (45KVA)
- Before the transformer, there needs to be a fusible disconnect, which will be located in a separate electrical box, mounted to the side of the machine tool.
- The Machine tool comes standard with a 125amp MCCB
- So the plant bus bar will have a power drop (4 wire) directly to the fusible disconnect. Then, I need to wire fusible disconnection -> transformer -> Machine tool MCCB.
- The wires running from the disconnect box to the transformer will be inside rigid conduit.
- The wire running from the transformer to the machine tool will be inside rigid conduit.
I did the following:
With the help of this site http://www.mikeholt.com/mojonewsarchive/NEC-HTML/HTML/TransformerInstallation~20020516.htm I did the following calculations:
Primary Current: 54.1 amps
Secondary Current: 124.9 amps
Primary Current Protection: 54.1*1.25 = 67.7 -> Next size up is 70 amp (Class J fuse is required).
Primary Conductor Size (Table 310.16)(will be using THHN, 90?C, copper): 6awg
- Because these are running thru conduit, do I need to apply a correction factor?
Primary Ground Size (Table 250.122): 8awg
- Based off 70amp current protection
**I have control of the wire type after the fusible disconnect, but before will be whatever the plant uses. Typically they use a cable, so in order to ensure adequate ampacities - should i spec the wire size and type taking into account the 80% correction factor (see below about wires in raceway/cable)?
Secondary Conductor Size(will be using THHN, 90?C, copper): ??awg
- This is where I get confused. My confusion comes from two things:
- 1) Because the machine has an MCCB, I would think it would be considered protection for the secondary side of the transformer. So with that, do you size the secondary conductors based off the MCCB or based off the FLA of the secondary side of the transformer? I know it's the same in my case, but this won't always be the case.
- Because there will be 4 wires are running through conduit (each phase and ground)- I think i need to apply a correction factor, however the correction factors are listed from "raceway" or "cable". Do i use the 80% correction factor anyways?
- So my initial shot would be: 125amp * 1.25 = 156.25amp *100/80 (correction) = 195.2amp -> Have to use 2/0 THHN wire
- Could the MCCB being secondary protection change the requirements on these conductors?
My next big area where I am confused is grounding/bonding.
- Per the above, right now, I have a power drop with an 8awg ground. This ground connects into the disconnect box(terminal block inside of the box). From the disconnect box, Another 8awg ground will run to the transformer where a grounding bar will be mounted to the inside of the transformer enclosure.
- So I am confused for what sizes I need for the following connections
- Transformer grounding strip -> X0 terminal on transformer (think I need 6awg based on area of hot ungrounded conductor on primary)
- Transformer grounding strip -> transformer case
- Transformer grounding strip -> Machine tool
Lastly, the machine tool came from the factory wired with 3awg (25mm?) wire from the MCCB to the first device (which is then daisy chained to other devices). I cannot see how this is ok as the ampacity of 3awg is 110amp at best (THHN @ 90?C). I would think I need to replace this with larger wires so that they are protected by the MCCB.
Sorry for the lengthy post. I just wanted to try and be as clear as possible and also show that I am trying to logically work thru this and not just get someone else to do all the work from me. Thanks for any and all help, I appreciate it!