Machine with a Tank Heater withot UL approval

Merry Christmas
Location
Germany
Occupation
Electrical Design Engineer / UL MTR
Hi guys, Here is Stephan, I'm an electrical desgin engineer from Germany and UL MTR of our company.
We are in the PanelShopProgram from UL Germany (NITW)

We are supposed to build a control cabinet for a machine according to UL/NFPA standard. Now the customer has a tank heater in the machine that does not have UL approval (permanently installed in a tank). Heater 920W 230V / 4A (We want to generate the voltage via a 480V / 230V transformer.

Are there exceptions for something like this in the NEC or NFPA79?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
UL508a only covers stuff that is in the control panel. The heater is not in the control panel so is outside the scope of UL508a.

There is no issue with providing controls and voltage for this heater from the control panel as long as you follow the rules for such controls.
 
Location
Germany
Occupation
Electrical Design Engineer / UL MTR
Hey Petersonra,
Yes, I know, the overcurrent protection of the heater is in accordance with the specifications of 31.6 Sizing of branch circuit protection for heater loads. Everything is fine in the control cabinet. I was just concerned about using devices in the field that do not have UL approval. And whether additional measures are required.
Okay thanks
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Hey Petersonra,
Yes, I know, the overcurrent protection of the heater is in accordance with the specifications of 31.6 Sizing of branch circuit protection for heater loads. Everything is fine in the control cabinet. I was just concerned about using devices in the field that do not have UL approval. And whether additional measures are required.
Okay thanks
There is an OSHA requirement that says all electrical equipment used in a work place must be listed by one of the NRTLs (Nationally Recognized Testing Laboratories), but that is rarely enforced. UL is just one of the NRTLs that can list the equipment.
 