Hello all,
Can someone please help me with my below questions ?
I have a Square D I-Line distribution panel with six breakers. There are 6 breakers in this I-Line distribution panel. Each breaker feeds one motor starter circuit. The connection is as shown below.
I-Line panel Feeder Breaker -> Fused Disconnect -> Starter Panel (with contactor & overload relay) -> Motor.
The distance between I-Line panel feeder breaker to starter panel is 30 to 40 feet. The starter panel has overload inside for thermal protection. The starter panel also has fused disconnect.
Question 1
Is it ok to use Motor Circuit Protector breaker with only magnetic trip in the I-Line panel ?
Question 2
Does the I-Line panel feeder breaker need to provide both thermal and magnetic protection ?
Question 3
Which section of NEC is applicable to this scenario ?
Question 4
Ideally when overload condition happens, the overload relay inside my starter panel will trip protecting the breaker and cable. In addition to this, should the I-Line feeder breaker provide thermal protection for cable running between I-Line panel and starter panel ?
Thanks & Regards,
Venkat
Can someone please help me with my below questions ?
I have a Square D I-Line distribution panel with six breakers. There are 6 breakers in this I-Line distribution panel. Each breaker feeds one motor starter circuit. The connection is as shown below.
I-Line panel Feeder Breaker -> Fused Disconnect -> Starter Panel (with contactor & overload relay) -> Motor.
The distance between I-Line panel feeder breaker to starter panel is 30 to 40 feet. The starter panel has overload inside for thermal protection. The starter panel also has fused disconnect.
Question 1
Is it ok to use Motor Circuit Protector breaker with only magnetic trip in the I-Line panel ?
Question 2
Does the I-Line panel feeder breaker need to provide both thermal and magnetic protection ?
Question 3
Which section of NEC is applicable to this scenario ?
Question 4
Ideally when overload condition happens, the overload relay inside my starter panel will trip protecting the breaker and cable. In addition to this, should the I-Line feeder breaker provide thermal protection for cable running between I-Line panel and starter panel ?
Thanks & Regards,