Hello I'm having trouble determining whether to model EMT as magnetic or non-magnetic in short circuit calculations as I know this will have an impact on an overall cable's impedance.

Is the majority of EMT out there magnetic rather than non magnetic or vice versa? Does the conduit being rigid or not play a role? Most of the time in the feeder schedules I am given show whether it's PVC or EMT and if it's rigid or not. Any tricks for how to make a sound assumption based on that information? Your help would be appreciated. Thanks!
 

ron

Senior Member
We typically model raceway as non-magnetic unless we know for sure it is magnetic.

Non-magnetic will provide worst case short circuit values. Arc Flash incident energies might end up not be worst case (higher fault current makes OCPDs open faster, thus sometimes lower level PPE called out), but you need to pick your poison.
 