IS IT REQUIRED BY CODE TO PROVIDED A MAIN BOND JUMPER FOR A MOBILE GENERATOR CONNECTION ?

MY ANSWER TO THIS IS NO BECAUSE THE MAIN BONDING JUMPER IS ESTABLISHED AT THE SERVICE ENTRANCE SWITCH GEAR, SOMEONE PLEASE CORRECT ME IF I'M WRONG !
 
Re: MAIN BOND JUMPER

Depends on the type of transfer, inclusive of the neutral or not.
Separately derived sources must have a n-g bond. If you transfer switch the neutral, then it is a SDS.
 