I have (10) sets of 600KCMIL conductors going to 4000A service. Per 250.29.D, we have to use minimum of 750KCMIL as main bonding jumber. Can I use parallal jumbers, in another word, can I run (2)400KCMIL instead of (1)750KCMIL? Thank you.
Sam34, If i read 310.4 right,only phase conductors,polarity conductors(DC),nuetral conductors,or grounded circuit conductors.I don't see main bonding jumpers.
Rick
I'm with George usually large service equipment comes with a equipment grounding bus and a busbar bonding jumper. But to answer your the requirement in 250.24(B) is for an "unspliced main bonding jumper". Would two conductors in parallel be considered one bonding jumper?
Thank you guys for your reply, I think it should comes with a equipment grounding bus and a busbar bonding jumper. Somewhat I thought we have to provide it our self. Is all service entrance equipment should come with bus bar bonding jumper? or at certain amperage rating? Thanks again
I have seen instances when large gear is ordered and someone forgets to mention it's going to be used as service equipment. No only is the MBJ missing, but the label listing it as service equipment is. Amazing how difficult it is to have that service equipment label field installed.