Re: Main Bonding Jumper 10-32 ampacity
Tom,
That is an interesting question. I see three different areas of interest. </font>
- <font size="2" face="Verdana, Helvetica, sans-serif">The 10/32 screw and the conductivity of its metal,</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">The effective cross section area of the enclosure metal which is smallest at the perimeter of the screw hole, and the enclosure metal conductivity,</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">The quality of the metal to metal contact between the screw and the enclosure.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"> Item 3 is the wild card that the manufacturer can only hope to influence with the installation instructions. When correctly installed, the quality of the connection can still be degraded by environmental factors at any time during the life of the installation.
The successful behavior of the 10/32 bond will, IMO, be nonlinear, a curve very similar to a fuse curve, just at slightly lower current vs. time levels. The bond will work until the connection quality degrades. The real test of the bond occurs under high current, short duration pulses. The pulse can climb until just before the metal melts.
The idea of a 10/32 ampacity has the underlying concept of steady state current and heat handling ability which I would equate with a red herring. I think its more important to look at the installation instructions, trust the background engineering and lab testing, and do a solid mechanical assembly.