george nicholson
Member
I have an existing entrance gutter that feeds 4 existing disconnects. It's all code from prior installation -- this work is not in question.
I am adding a 5th fused swritch. The service entrance neutral is bonded to the ground system inside the gutter. There are separate ground terminals and neutral terminals in the gutter. I can NOT run a ground thru the utility companies CT meter can.
Here is what I want to do but I am told its incorrect:
1) add a 400A power company CT meter can connected to the gutter with rigid. The 3 phase conductorsand 1 neutral only are allowed to travel thru the utility can. No bonding or grounding in the CT meter can. Its all connecetd with rigid pipe.
2) Feed out of the CT can thru rigid into a 400A fused switch with the neutral and 3 phase conductors. (750XHHW alum)
2) add a ground lug to the fused switch with green screw tapped to switch can and jump from it to the neutral lug with 2/0 copper.
3) leave the switch with PVC and run 100' to a gutter that has 2 MB load centers with the 3 phase conductors, the neutral, and a green #4 EGC. The green gEGC is #4 copper and its connected to the ground terminal on the switch can as its origin.
4) At the metal gutter where the 2ea 200A MB load centers are located the green #4 EGC is terminated at a ground terminal tapped to the gutter with a green screw.
5) The MB load centers are connecetd with emt to the metal gutter. The 3 phase conductors and neutral are connecetd to the load center and the neutral is NOT bonded to the can or ground at this end.
6) There is a separate ground terminal in the load center tapped to the load center can from factory and its is used for required equipment grounds leaving the load center but is not bonded to any conduits or the terminal strip in the gutter.
What is wrong with this install. Assume the existing entrance gutter and all work inside it are OK.
This was turned down but we are told only that the bonding and grounding is inadequate at the CT and fused switch? I was told the fused disconnect should have neutral and ground bonded as if it was the first point of entry.
Any suggestions?
I am adding a 5th fused swritch. The service entrance neutral is bonded to the ground system inside the gutter. There are separate ground terminals and neutral terminals in the gutter. I can NOT run a ground thru the utility companies CT meter can.
Here is what I want to do but I am told its incorrect:
1) add a 400A power company CT meter can connected to the gutter with rigid. The 3 phase conductorsand 1 neutral only are allowed to travel thru the utility can. No bonding or grounding in the CT meter can. Its all connecetd with rigid pipe.
2) Feed out of the CT can thru rigid into a 400A fused switch with the neutral and 3 phase conductors. (750XHHW alum)
2) add a ground lug to the fused switch with green screw tapped to switch can and jump from it to the neutral lug with 2/0 copper.
3) leave the switch with PVC and run 100' to a gutter that has 2 MB load centers with the 3 phase conductors, the neutral, and a green #4 EGC. The green gEGC is #4 copper and its connected to the ground terminal on the switch can as its origin.
4) At the metal gutter where the 2ea 200A MB load centers are located the green #4 EGC is terminated at a ground terminal tapped to the gutter with a green screw.
5) The MB load centers are connecetd with emt to the metal gutter. The 3 phase conductors and neutral are connecetd to the load center and the neutral is NOT bonded to the can or ground at this end.
6) There is a separate ground terminal in the load center tapped to the load center can from factory and its is used for required equipment grounds leaving the load center but is not bonded to any conduits or the terminal strip in the gutter.
What is wrong with this install. Assume the existing entrance gutter and all work inside it are OK.
This was turned down but we are told only that the bonding and grounding is inadequate at the CT and fused switch? I was told the fused disconnect should have neutral and ground bonded as if it was the first point of entry.
Any suggestions?