Hi folks,
This is a follow up question related to an open topic way over in the PV Forum.
What are the available avenues for requesting a formal interpretation of an article in the NEC?
I am currently assembling some published articles and relevant code sections to forward to the DCA in NJ, with the intent of clarifying the PV industry best-practice (I believe the only code-compliant method) of bonding the grounded conductor at the PV system disconnect, when using a supply side connection.
All of the published material I can find, as well as the feedback I am getting from my contacts in the industry, indicate that this enclosure should be treated as a service disconnect, which is installed to disconnect an explicitly permitted "set" of service entrance conductors. The DCA's stance is that since PV is not a "service", no sections of article 230 would apply, and the grounded conductor should not be bonded in this enclosure.
Your thoughts?
I humbly ask the moderator to allow this post here, as I am soliciting the response of a broader knowledge base. I'm preaching to the choir in the PV chamber! I'm happy to provide code references, but I'd rather not lead the witness.
Thanks
This is a follow up question related to an open topic way over in the PV Forum.
What are the available avenues for requesting a formal interpretation of an article in the NEC?
I am currently assembling some published articles and relevant code sections to forward to the DCA in NJ, with the intent of clarifying the PV industry best-practice (I believe the only code-compliant method) of bonding the grounded conductor at the PV system disconnect, when using a supply side connection.
All of the published material I can find, as well as the feedback I am getting from my contacts in the industry, indicate that this enclosure should be treated as a service disconnect, which is installed to disconnect an explicitly permitted "set" of service entrance conductors. The DCA's stance is that since PV is not a "service", no sections of article 230 would apply, and the grounded conductor should not be bonded in this enclosure.
Your thoughts?
I humbly ask the moderator to allow this post here, as I am soliciting the response of a broader knowledge base. I'm preaching to the choir in the PV chamber! I'm happy to provide code references, but I'd rather not lead the witness.
Thanks