Main Bonding Jumper

Status
Not open for further replies.

KLM

Member
Location
Orlando, Fl
Please refer to the diagram below. Is it acceptable for the main bonding jumper to be located at the utility company transformer? I see nothing wrong with the concept and it would be allowed by code if it were considered separately derived system. Since it is considered a service, does the main bonding jumper have to be located at the service disconnecting means?


grounding3.jpg
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Most utilities will not allow the equipment ground shown in your diagram to be in their equipment. They bond everything to the neutral, so the equipment ground would be a paralell path.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Most utilities will not allow the equipment ground shown in your diagram to be in their equipment. They bond everything to the neutral, so the equipment ground would be a parallel path.

I agree, remove the EGC and you're OK since the neutral can be used for grounding on the line size of the service disconnect.
 