Hi all, couple questions mainly concerning ground fault protection - this is my first design implementing GFP on a system wide level.
Here is the scenario:
A transformer in a supervised location with a primary over 1000V and secondary below 1000V feeding a switch gear with 3 feeder breakers. The primary will be protected by fuses.
Using 450.3a the primary side fuses can be up to 250% of the transformer current rating, and no overcurrent protection required on the secondary.
Is there merit to a secondary side main breaker in the switch gear?
Do I need it to provide GFP?
Can GFP be adequately achieved using only the feeder breakers?
Thanks for your input.