Hi all, couple questions mainly concerning ground fault protection - this is my first design implementing GFP on a system wide level.
Here is the scenario:
A transformer in a supervised location with a primary over 1000V and secondary below 1000V feeding a switch gear with 3 feeder breakers. The primary will be protected by fuses.
Using 450.3a the primary side fuses can be up to 250% of the transformer current rating, and no overcurrent protection required on the secondary.
Is there merit to a secondary side main breaker in the switch gear?
Do I need it to provide GFP?
Can GFP be adequately achieved using only the feeder breakers?

Thanks for your input.
 
Ground faults are most likely to occur on the feeders, so they should have GFP regardless if you have a single secondary main device with GFP.
 
You could put gf relays on the feeders and use them to trip the main breaker. But then you get a single downstream gf and all your feeders are off.
 
Thanks for the replies... Does the G in an LSIG breaker cover this without the need of relays/sensors?
 