Per Art. 220.18 (A) three 17 amps motors can be feed from one circuit breaker (CB). Size of CB is 1.25 times largest motor load + other motors or 1.25 x 17 +17+17 = 55 amps or 60 amp CB in this example. However the VFD equipment manufacturer I am working with says the three panel VFD requires an 80 amp CB according to UL508? Does anyone know why UL508 is requiring a larger CB?
Should I assume UL508 will supersede NFPA 70 on this subject?
Should I assume UL508 will supersede NFPA 70 on this subject?