main breaker for Panel

Status
Not open for further replies.

Leo Li

Member
Location
China
Occupation
Engineer
As below showing there is no main brealer for panel DPEM3(circled with red), I wolud like to know if this is isolation from NEC and actually I can't find related item for this. Thanks! DPEM PANEL.PNG
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I didn't find but it will lose disconnecting means for panel DPEM3.
I don't see a problem with this arrangement. The 400 amp feeder breaker protects the bus in this panel board and serves as a disconnecting means if needed. The code never requires a main breaker to my knowledge.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Are both panels in the same building. If so I agree with petersonra
 

Leo Li

Member
Location
China
Occupation
Engineer
Are both panels in the same building. If so I agree with petersonra
They are in the same building but not in the same room. Other panel's main breaker is available but only this panel main breaker is missing. I didn't know the reason and don't know if this isolation code. Thanks !
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Here's the relevant code section. The OCPD can be at the origin of the feeder and is not required to be in the panelboard.

408.36 Overcurrent Protection. In addition to the requirement of 408.30, a panelboard shall be protected by an overcurrent protective device having a rating not greater than that of the panelboard. This overcurrent protective device shall be located within or at any point on the supply side of the panelboard.
 

Leo Li

Member
Location
China
Occupation
Engineer
Here's the relevant code section. The OCPD can be at the origin of the feeder and is not required to be in the panelboard.
This is clear for me now. But I prefer to put main breaker inside this panel to easy disconnection and miantenance this panel. Thanks!
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
This is clear for me now. But I prefer to put main breaker inside this panel to easy disconnection and miantenance this panel. Thanks!
That's a common reason for MCB's in panels but it's a design issue not a code issue. I've seen value engineering where they remove the 400 amp main in the panel to save the cost of a 400 amp CB.
 