jetlag
Senior Member
- Location
- Eatonton, Georgia
Do you have to have a main breaker in a temporary service box if it has no more than 6 - 20 amp breakers that don't exceed the 125 amp box or the # 2 copper S E cable .?
I agree with mbednarik... The 2020 nec requires a main in your situation.Do you have to have a main breaker in a temporary service box if it has no more than 6 - 20 amp breakers that don't exceed the 125 amp box or the # 2 copper S E cable .?
ok thanks , I hope it is ok to back feed a 60 amp breaker on the buss for the main . That will be plenty of power . I was thinking the other way that the breakers would count as the disconnect if you can kill the power with 6 or less switches .
thanks Kwred . do they have a universal hold down for one inch spaced breakers with a double pole to hold down ? It is a homeline box . Can you buy a cover also or use something else ?The reason the ruled changed was because there was no way to work on the panel safely because you can never kill the power to the bussbar.
If you back feed a panel that would work but you would need a hold down kit and you would need to be able to cover the lugs on the breaker so they are not exposed.
Most RV pedestals are installed on feeders, so there's an upstream disconnect & OCPD. (Are any of them suitable for use as service equipment? I don't think I've ever looked.)I have installed a lot of RV boxes...
If separate structure, will need disconnect, often accomplished by using MBP rather than MLPIt is still ok to use a sub panel with out a main disconnect if the feeder to it has a breaker in the main panel isn't it ?
There should maybe be some sort of exception for an enclosure designed to house a single overcurrent device as well?I think there should be exceptions for temp services. Here, we use a temp panel that has either a 50A and 20A breaker, or just a 20A breaker. The panels are MLO. The rule for the requirement is so power to the bus can be turned off if you need to work in there. On a temp panel, you shouldn't need to be working in it. It is just to provide power for construction purposes. You set it up and done.
We are still on the 2017 and it's not required. Inspectors here say they won't require a main on temp panels should we adopt the newer codes.
True. Most "loadcenters" I have seen have such marking on them.For installations under the older codes, you have to look at the panel instructions. There are small panels that are marked "suitable for use as service equipment only where a main breaker is installed".
Even though the equipment is labeled as such, anything installed under a 2020 NEC still requires a main.True. Most "loadcenters" I have seen have such marking on them.
Only panel I can recall using that I know is ok to use as service equipment with main lug only supply is an I-line panel, but there likely is some others.
yesEven though the equipment is labeled as such, anything installed under a 2020 NEC still requires a main.
🫣I think there should be exceptions for temp services. Here, we use a temp panel that has either a 50A and 20A breaker, or just a 20A breaker. The panels are MLO. The rule for the requirement is so power to the bus can be turned off if you need to work in there. On a temp panel, you shouldn't need to be working in it. It is just to provide power for construction purposes. You set it up and done.
We are still on the 2017 and it's not required. Inspectors here say they won't require a main on temp panels should we adopt the newer codes.
Which leads to the unfortunate confusion as to whether that means:For installations under the older codes, you have to look at the panel instructions. There are small panels that are marked "suitable for use as service equipment only where a main breaker is installed".