Osomxl
Member
- Location
- Mexicali Mexico, Baja california
My question is regarding the following setup. Keep in mind I live in Mexico and the house is concrete block construction.
main breaker at the meter is two 60 amp breakers and both of these wires are 6 awg black. The ground was wired in red 8awg and leaves the main breaker box and is grounded to a ground rod directly below the meter socket main and follows the two hot conductors and are then bonded inside the house at the breaker panel with all the neutrals and grounds on the busbar.
I am in the process of installing a subpanel outside in preparation for an addition as my current panel is full and have no way to come off the existing panel without knocking a hole in the concrete block wall and running exterior conduit on the side of the house.
I have just installed conduit in the ground and was planning on coming into the side of the meter main.
I now think I should separate the neutral and grounds in the breaker box and bond the ground and add a neutral at the breaker main that goes back to the breaker box and add a neutral bus there as well.
My next predicament is how to add the new sub panel to the meter main which is rated for 100 amps and currently only has the two spaces which are occupied by the current sub panels 60 amp breakers without changing to 100 amp breakers and landing both subs under the same lugs.
I didn't want to change out the meter main, but at this moment it may be my best option.
My house here in mex is nowhere near being code compliant, but I do like to try and do it right as I remodel. Anybody with some oversight or options would've be greatly appreciated.
main breaker at the meter is two 60 amp breakers and both of these wires are 6 awg black. The ground was wired in red 8awg and leaves the main breaker box and is grounded to a ground rod directly below the meter socket main and follows the two hot conductors and are then bonded inside the house at the breaker panel with all the neutrals and grounds on the busbar.
I am in the process of installing a subpanel outside in preparation for an addition as my current panel is full and have no way to come off the existing panel without knocking a hole in the concrete block wall and running exterior conduit on the side of the house.
I have just installed conduit in the ground and was planning on coming into the side of the meter main.
I now think I should separate the neutral and grounds in the breaker box and bond the ground and add a neutral at the breaker main that goes back to the breaker box and add a neutral bus there as well.
My next predicament is how to add the new sub panel to the meter main which is rated for 100 amps and currently only has the two spaces which are occupied by the current sub panels 60 amp breakers without changing to 100 amp breakers and landing both subs under the same lugs.
I didn't want to change out the meter main, but at this moment it may be my best option.
My house here in mex is nowhere near being code compliant, but I do like to try and do it right as I remodel. Anybody with some oversight or options would've be greatly appreciated.