Re: Main Breaker Outside?
I think the key word is recommends. I'm not sure why they would recommend this; it's certainly not common in my area. The NEC does require that the service have its disconnecting means either outside the building or "inside nearest the point of entrance of the service conductors." If you install an outdoor main, that will allow you to enter the house with the service conductors anywhere and then continue inside to anyplace you like for your panel. Without the outdoor main, you have to have your main panel right where the service entrance conductors come inside, or have a disconnecting means there and then a subpanel for your branch circuits.
The only time I've installed an outdoor main was when the homeowner didn't want the main panel right where the service entrance conductors came in, so the AHJ required the outdoor switch. My price at the supply house for the 200A Siemens breaker and the enclosure for it was $350.