Went on a service call to check the power in the garage, the garage door installer say he had 99 volts at the outlet. So by the time I got there the main breaker in the panel was off.
Read voltage between the two legs coming in and read 247v and between one leg and neutral 123v and same on other. Turn the breaker on and read the bus bars and 247v between the two and 99v on one and 148 on the other, no loads on at this time all branch circuits off. Read the two lugs before the main and get the same readings as on the bus, turn the breaker off and readings go back to correct, turn breaker on and readings are off.
Question is, is the main on this panel bad or could a bad neutral be causing this?
“ shoot low boys their riding shetland ponies”
Read voltage between the two legs coming in and read 247v and between one leg and neutral 123v and same on other. Turn the breaker on and read the bus bars and 247v between the two and 99v on one and 148 on the other, no loads on at this time all branch circuits off. Read the two lugs before the main and get the same readings as on the bus, turn the breaker off and readings go back to correct, turn breaker on and readings are off.