I work for an electric utility. We are using meter sockets that are UL listed at 320 amps continuous and 400 amps maximum. I have had conversations with a licensed electrician concerning amp ratings of a main breaker. It is now my understanding that a 400 amp breaker rating means that 400 amps is a "maximum" rating and that the continuous rating is 20% or 80 amps less which puts it at 320.
The way we currently handle services with main service breakers of 400 amps for example is not to use the 320 amp socket but meter it with current transformers.
What I am trying to determine is whether I can issue the electrician a 320 amp UL listed socket when he is installing a 400 amp main and not violate any NEC requirements.
The way we currently handle services with main service breakers of 400 amps for example is not to use the 320 amp socket but meter it with current transformers.
What I am trying to determine is whether I can issue the electrician a 320 amp UL listed socket when he is installing a 400 amp main and not violate any NEC requirements.