Where you get into a problem is when you are protecting this panel on the "supply" side with a single disconnect or 2 pole disconnect...which then exception 2 comes into play.
All panelboards are to be protected ?at not greater than? their rating by a single overcurrent protective device within or ahead of the panelboard. The distinction here is the term "single? is what sets this apart from the exceptions like #2 below. Now let?s look at the exceptions to this rule.
If the new panel is in the same building, no breaker required.
408.36 Overcurrent Protection.
In addition to the requirement of 408.30, a panelboard shall be protected by an overcurrent protective device having a rating not greater than that of the panelboard. This overcurrent protective device shall be located within or at any point on the supply side of the panelboard.