So I did the optional method to determine the main service for a 8 unit apartment building. I came up with a demand load of 99kva. So a 600A service will be installed. I'm a little confused on how to determine the panel size for the individual units. Do I use the standard method and treat each unit as a single family?
My other question is this: let's say I have a demand load of 21.5kva. On 120/240 that's 89.5A. Do I need to multiply that by 125% like you normally do for a branch breaker? Would I need more than 100a feeder to each unit is basically what I'm asking, but i've been confused on doing load calls for years. Too much single fam resi.
My other question is this: let's say I have a demand load of 21.5kva. On 120/240 that's 89.5A. Do I need to multiply that by 125% like you normally do for a branch breaker? Would I need more than 100a feeder to each unit is basically what I'm asking, but i've been confused on doing load calls for years. Too much single fam resi.