main breaker sizing

Status
Not open for further replies.

DrSparks

The Everlasting Know-it-all!
Location
Madison, WI, USA
Occupation
Master Electrician and General Contractor
So I did the optional method to determine the main service for a 8 unit apartment building. I came up with a demand load of 99kva. So a 600A service will be installed. I'm a little confused on how to determine the panel size for the individual units. Do I use the standard method and treat each unit as a single family?

My other question is this: let's say I have a demand load of 21.5kva. On 120/240 that's 89.5A. Do I need to multiply that by 125% like you normally do for a branch breaker? Would I need more than 100a feeder to each unit is basically what I'm asking, but i've been confused on doing load calls for years. Too much single fam resi.
 
You can use either standard or optional method for each unit.

You only add 25% for continuous loads and the largest motor. Typically, there is no continuous load in dwelling calc's.
 
So you would go with 100A panels and breakers with a demand load of 89A? I neglected to mention that each unit has 6500W of electric heat.
 
So you would go with 100A panels and breakers with a demand load of 89A? I neglected to mention that each unit has 6500W of electric heat.
And if your 6500W of heat operates continuously at max' current for 3 hours or more, it is seriously undersized (unless we enter into a new ice age :p)... so still not a continuous load that needs to be factored at 125%.

100A panels looks good to me. :happyyes:
 
Yeah and 6500W is the sum of the nameplates of 6 separately controlled units. So I agree. Thanks a lot for your help!
 
The 99KVA seems high if you only have 8 units @21KVA. Are you sure you used all of the demand factors in the service calculation?
 
The 99KVA seems high if you only have 8 units @21KVA. Are you sure you used all of the demand factors in the service calculation?

Well, here's the breakdown:

Gen light: 21,505 s.f. x 3va = 64.5k
Small appl + laundry = 4.5k x 8 = 36k
Water heaters = 4.5k x 8 = 36k
Dryers = 5k x 7 = 35k
Ranges = 10k x 7 = 70k
Heat = 6.5k x 8 = 52k (6 separately controlled units)

Total connected load = 229k
Optional method demand load = 229k x 0.43 = 99k
Amps = 99k / 240 = 412.5A

Sound right?
 