Hey Guys,
I am sizing a panel board, where 2 inverters with 150A (120A x 1.25) breakers supply the bus, and the same panel board have the provision for monitoring as well with 2 15 A breakers. So I sized the bus as the sum of all the breakers (150+150+15+15 = Round off to 400A) and my question is - can the main breaker in this panel board be 300A or should it be 400A? because only the inverters supply the bus and the monitoring devices are loads. (Please check attached)
Hey Guys,
I am sizing a panel board, where 2 inverters with 150A (120A x 1.25) breakers supply the bus, and the same panel board have the provision for monitoring as well with 2 15 A breakers. So I sized the bus as the sum of all the breakers (150+150+15+15 = Round off to 400A) and my question is - can the main breaker in this panel board be 300A or should it be 400A? because only the inverters supply the bus and the monitoring devices are loads. (Please check attached)