I designed a project with an existing panel loaded close to max amp rating. The panel is filled with HVAC loads (rooftop units with DX cooling).
It is a 460v/3ph, 200 A panel and my total FLA calculates to be 195 A total which includes 25% of the largest motor (a compressor in one of the RTUs). I did not assume any load was a continous load since HVAC loads generally arent continous load from my undersrtanding. The panel main breaker is currently tripping in the afternoon with the recent heat.
Looking at the building automation system the RTUs aren't even operating at 100% cooling capacity. The main breaker has trip settings but my understanding is you shouldn't be adjusting those settings without a coordination study.
It is a 460v/3ph, 200 A panel and my total FLA calculates to be 195 A total which includes 25% of the largest motor (a compressor in one of the RTUs). I did not assume any load was a continous load since HVAC loads generally arent continous load from my undersrtanding. The panel main breaker is currently tripping in the afternoon with the recent heat.