I have a main breaker feeding a subpanel approx 90' away in EMT conduit. Main breaker is a 250amp Square D with electronic trip unit Micrologic 6.0A. The load is 10 heaters in VAV boxes that are used very little.
The problem is that the breaker trips once in a blue moon mostly at night when no one is around. I have meggered the wire and get readings to eachother and ground over 16G Ohms at 500V @ 5min time. None of the branch circuit breakers has ever tripped. I have rasised the trip ratings to max and it still trips the breaker, installed new breaker and still tripped.