Re: main breaker
Depends on a lot of things, such as: what are these loads, which loads are continuous in nature, what type occupancy or facility is this,where is the money coming from, etc.
Important to read NEC definition of continuous load closely. "The maximum current- - -". Usually this is a load like the general lighting in most commercial/industrial occupancies.
There are some loads that are actually in operation for 3 hours or more but are not continuously drawing their maximum current.
If your 560A figure takes into account all the Art.220 rules, then a standard 600A molded case bkr. is probably okay. But remember their is little room for any future loads though.
I believe the "somebodies" rules require a plain Jane 600A molded case bkr. to be able to carry 80% of its rating (480A) continuously. There are also 700A bkrs.