Main Breakers mounted in remote enclosures.

Status
Not open for further replies.

bryanintikrit

New member
Guys,
I have a sub contractor that is installing a generator fed 3 phase grid. Power comes from the generator to the Main Distribution panel. All wiring and breakers are within correct load requirements as far as breaker size and wire load rating. The MDP is equipped with a main breaker and sub breakers to feed the sub panels.The sub panels that are fed out of the MDP do not have main breakers but the cables are terminated directly to the buss bars (where a main breaker would normally be installed)that feed the branch circuits. All of this equipment is in "line of sight" and properly labeled. I like to see a main breaker in the sub panels. Does the code prohibit this practice?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Re: Main Breakers mounted in remote enclosures.

Since the feeders to the subpanels are properly protected at the MDP no further protection is required at the subpanels. Unless these panels were located at a separate building(s) than they would require a disconnecting means at that building.
 

wirenut1980

Senior Member
Location
Plainfield, IN
Re: Main Breakers mounted in remote enclosures.

As infinity has said, it is not required, and since it is not prohibited, it is allowed...but IMO not necessary. :)
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Re: Main Breakers mounted in remote enclosures.

The sub-panels do not even have to be "line of sight." They can be on other floors, and they still would not require a main breaker at the panel.
 