The load side conductors from the bus duct must be protected within their ampacity. If your bus duct switch is fused, size your fuses per 310.16 (assuming cabling is used).
If bus duct switch is unfused, you may view its load side conductors as a tap, in which case tap rules apply (240.21.....). Another factor in sizing your TX Primary side OCPD (Transformer Over Current Protective Device) is whether you will choose to install a transformer secondary OCPD (fuse or breaker) OR just the primary (450.3(B)). A transformer secondary OCPD can serve as both a TX secondary OCPD and a Line side panel OCPD (see 450, 408, 240 etc)
Additionally as other folks mentioned above, you must provide for a line side disconnecting means for the panel (which may be fused and serve as a TX secondary OCPD as per above) if any of the following apply:
The panel is in another room
The panel is out of line of sight from the TX primary OCPD
The panel is to be used as a lighting and appliance panelboard (408.16); Farther than 50 feet (Article 100)