This was one code that bounced all over the NEC till they finally settled it into the present place of 408.36, it was in 384-16 in the 1999 NEC and was moved to 408.15 in the 2002 with some words changed, then in 2005 it was located in 408.36 with no changes to the wording, but the 2008 made a complete over haul of 408.36 along with the description of what a Lighting and Appliance Branch-Circuit Panelboard was, which was removed along with the 42 space requirement, the 2011 kept the 2008 wording intact.
So basically we went from having two different types of panel boards by the description of a Lighting and Appliance Branch-Circuit Panelboard, which required protection and the 42 breaker space limit and a power panelboard that only had line to line loads didn't require protection, but was only allowed 6 breaker handles, sub-panels still have the 42 space limitation (exception 2 to 408.36).
To now only having either a main breaker panelboard lug fed panelboard, or a service rated panelboard under the exception to 408.36 exception 1
along with eliminating the 42 space requirement unless you install it as a sub-panel (408.36 Exception 2) they also eliminated the definition of lighting and appliance branch-circuit panelboards
This section really confuse many during these changes.