Commercial building. Have an existing electrical room in a basement on an exterior wall. Changing out the service. Existing service is in room, on exterior wall. The new service will go on adjacent (interior) wall. Service entrance conduit will have to run about ten feet through the room before getting to main disconnect in new service equipment. We have the ability to cut and trench the floor to get to the new equipment, but would rather go through the ceiling space.
In your experience do service feeders cutting about ten feet across an electrical room need to be 2-hr concrete encased (per 230.6)? Or is 230.70(A)(1) ("disc shall be installed at a readily accessible location...nearest the point of entrance of the service conductors") interpreted generously enough to allow these to be ran w/o concrete encasement? For what it's worth, this is the "nearest readily accessible location" in the room.
I'll ultimately run this by the local inspector, right now am just looking for the experiences of others to start a preliminary design. Thanks!
In your experience do service feeders cutting about ten feet across an electrical room need to be 2-hr concrete encased (per 230.6)? Or is 230.70(A)(1) ("disc shall be installed at a readily accessible location...nearest the point of entrance of the service conductors") interpreted generously enough to allow these to be ran w/o concrete encasement? For what it's worth, this is the "nearest readily accessible location" in the room.